New Guy Posted June 24, 2023 Share Posted June 24, 2023 Hey, Can someone please tell why there is 30 sec time out during priming and cross feed operation. like what is the relevance of 30 sec timeout. Regarda Quote Link to comment Share on other sites More sharing options...
NATOPS1 Posted July 25, 2023 Share Posted July 25, 2023 Allows enough fuel to flow through the manifold to remove (push) any air "Priming" means removing the air. Quote Link to comment Share on other sites More sharing options...
New Guy Posted August 2, 2023 Author Share Posted August 2, 2023 Thanx for the reply, I am aware of it, I was just curious why only 30 sec, why not 1 min or any other timing. Rhanx Quote Link to comment Share on other sites More sharing options...
NATOPS1 Posted August 19, 2023 Share Posted August 19, 2023 Some non operator somewhere calculated the flow rate and figured it was long enough based on the size of the pipes... But FWIW based on the pump rated output and the size of the pipe as well as the distance needed to travel one could (or has) figure out how much time is needed. Quote Link to comment Share on other sites More sharing options...
New Guy Posted September 5, 2023 Author Share Posted September 5, 2023 Thank you Quote Link to comment Share on other sites More sharing options...
victorp1 Posted September 12, 2023 Share Posted September 12, 2023 Using a Flow vs Pressure chart, at 24 PSI flow thru the primer valve should be approximately 7 US gallons in 30 seconds. Quote Link to comment Share on other sites More sharing options...